I also forgot to mention the reactive power factor charges.
Sent from my VS987 using Tapatalk
Sent from my VS987 using Tapatalk
Yep. I agree with that. Let the utility pay for upkeep and energy consumtion. It may be low - around 2% but why pay for it if you don't have to...In my opinion let the utility own it.
They will handle replacement, the running costs etc.
On the other hand if the customer owns it the customer will also have to provide and handle the upkeep of a MV service disconnect and OCP.
I see no benefit at all unless the customer has other uses for MV
Besoeker2?
It means visitor.Besoeker2?
Same Besoeker but just a more newly established version? :blink:
This is usually what I see as well. Large industrial commercial/industrial complex that has a utility service entrance at the distribution voltage and then overhead lines that drop down into various service entrances. Are these really considered service entrances anymore if all these service entrances are behind the main utility meter where the overhead lines come onto the property? I have seen cases where the utility lines come onto the property, hit a utility meter and then travel overhead on property to various riser poles where there are gang operated switches, and fused cut-outs before it drops down to a transformer. What is considered the "service entrance" in this case?
Besoeker2?
Same Besoeker but just a more newly established version? :blink:
Nice to know... but I was asking for verification that the patron posting or having posted as Besoeker is, in fact, you, Besoeker2.It means visitor.
Friends call me Mac.
Nice to know... but I was asking for verification that the patron posting or having posted as Besoeker is, in fact, you, Besoeker2.
Let's not expand the topic............He is the same pain in the rear ....
He is the same pain in the rear ....
Well said that man.Please stay on the topic of transformer ownership.
We can move to a new thread if you would like to discuss forum policies.
He is the same pain in the rear ....
I dont think that would fly. I think you would have multiple issues with definitions of various things. Also I am not sure if these transformer integral disconnects are rated for load breaking? Maybe others will have some comments here.
I cant seem to find anything in the NEC that would prevent using this internal VFI switch as the service disconnect. In fact Exhibit 230.30 in the 2014 NEC handbook appears to illustrate this exact case with the service disconnect integral to the customer owned transformer.
I did check and this switch is rated for load breaking capacity.
So what defines exactly where the "service point" is weather its on the primary or secondary. Is this usually recognized as wherever the utility has their metering installed?
A fair number of electrical contractors (especially smaller ones) are not well experienced in dealing with MV so you may wish to make it the POCO's problem.
That’s a problem wherever you are. Before I retired, every three years I had to go on a training course with the local DNO (PoCo) to carry out switching operations. Does the US have a similar system?
Our electrical regulations BS7671 don’t cover MV, you have to follow BS7430 (private network operator code of practice).
That’s a problem wherever you are.
Not really sure what you mean. Thats the way it is in the states. Most electricians and EC's dont do MV work. I can pull MV cables and put on a load break elbow, but thats about it for me.