lakee911
Senior Member
- Location
- Columbus, OH
The other day I came across an indicating lamp, with no OCPD, that was wired across the line side of a service's main breaker. The intention was to provide indication that utility power was available regardless whether the main was opened or closed. The main breaker was interlocked with a manufacturer provided kit to allow back-feeding through a branch breaker for standby power.
I couldn't think of a good inexpensive solution to fixing the problem short of adding a new 200 service rated breaker upstream of that panel and then utilizing the tap rule to bring out another set of conductors, with OCPD, to the lamp. So, then I thought, why couldn't this be done right on the service? We're limited to six disconnects, but it would only be two in this case.
Thoughts?
I couldn't think of a good inexpensive solution to fixing the problem short of adding a new 200 service rated breaker upstream of that panel and then utilizing the tap rule to bring out another set of conductors, with OCPD, to the lamp. So, then I thought, why couldn't this be done right on the service? We're limited to six disconnects, but it would only be two in this case.