If available fault current is 30kA at transformer terminals, and that overhead quad is only 1/0 AWG (seems to be common size and it sort of looks to be about that from pic) I put this information into the fault current calculator that is on Mike Holt's free stuff page and with only 50 feet of quad that 30kA is nearly cut in half a the load end.I don't see why. I am usually able to obtain the available primary fault current (3ph & SLG), associated X/R, fuse data, transformer data, riser cable (if padmount txf) from the utility without a challenge. Larger utilities may take a month to turn the request around but only once did I have an issue. I ended up filing a complaint with the state PUC and the utility eventually relented.
I think you mean secondary impedance. Assuming a 2% impedance on the dist pots, this is a fault current of about 30kA at the txf sec terminals. I don't think you will get a significant reduction in fault current with the secondary quadraplex. If you are using the infinite bus, I think your equipment should be rated for greater than 30kA
IMO that quad is where the most drop in fault current will likely be and how much all depends on it's length.