- Placerville, CA, USA
- Retired PV System Designer
Interesting Catch 22 they get you in there:Xcel Energy has this clause in the service book"
"If the customer?s power requirement, within six months after the installation of transformers, proves to be less than shown in the application for service, the Company may make a reduction in the installed transformer capacity and the customer will be required to pay the Company the cost of making the change.
If the customer?s power requirement, within six months after the installation of transformers, proves to be more than the installed transformer capacity, the Company may make an increase in the installed transformer capacity and the customer will be required to pay to the Company the cost of making the change."
In their territory you would not want to 'mis-size' your service on your permit application, as you did in your example, it could come back and cost you.
Regardless the point still is, that utilities have their own methods for determining the size of their service equipment.
You give them an estimated load in your application and if you are 1kW lower than that, you might end up paying. While if you underestimate and you are still within the capacity of whatever size transformer they chose to install, then you are still OK.
But if for any reason they choose to install a transformer with a lower capacity than your stated load (as it is within their power to do) then you are still screwed if you actually use what you stated. :blink: