So, does your utility install 3PH reclosers on every 3PH bank no matter the size? Seems like that would be cost prohibitive. I could understand perhaps installing a 3PH recloser on circuits with a known ferro issue (like after several bank failures). However, it seems like there are cheaper ways to de-tune the circuit.
There is no need to. Small banks (under 750kva) are connected to the 12.47 or 13.8kv distribution system which usually has an MGN allowing wye-wye transformers; or in small cases where delta-wye is used the risk is considered minimal at that voltage.
However, large facilities like malls and factories require transformer banks over 1000kva, feeding such intensive loads from 12kv distribution circuits is not practical for a variety of reasons. 23, 27 and 34.5kv sub-transmission circuits are used. These circuits do not have an MGN, therefore any load must be connected phase to phase. Delta-wye transformers are always used. Both the size of the customer (kwh), and the amount of equipment that might be damaged (CNC machines) make a 3 phase recloser cost justifiable.
Cost analysis is was done on cheaper methods like 3 phase air break switches (which are used on some older facilities rather than recloser for line men switching), and running an MGN on sub-transmission circuits but that idea was rejected due to cost and vector voltage shift associated with wye connected voltage regulators on long lines.
Also, this might be off scope, but some large critical facilities are forced to use reclosers anyways in auto source transfer applications, so having reclosers mitigate ferroresonance is a welcome compliment.