I'm wiring up a RV service for a buddy. I've been an onsite company electrician in an industrial facility for several years now and not really current as to normal procedure for this situation. So I was wondering about something.
He gave me the paper work from the utility for what he needs and it states that the utility is going to run 4awg 200ft to the meter for a 200A service. I know utilities don't use the NEC but this seems wrong. 4awg for a 200A service seems way to small. Is it normal for a RV or mobile home service?
I'm bringing 2/0 w/a 4awg grounded conductor from the meter to the service disconnect and a 4awg GEC to the rods.
Thanks.
He gave me the paper work from the utility for what he needs and it states that the utility is going to run 4awg 200ft to the meter for a 200A service. I know utilities don't use the NEC but this seems wrong. 4awg for a 200A service seems way to small. Is it normal for a RV or mobile home service?
I'm bringing 2/0 w/a 4awg grounded conductor from the meter to the service disconnect and a 4awg GEC to the rods.