I'd think we'd actually need to look into 551 and 310.15(b)7 is actually for dwelling units which in my book an RV is not.
Good point, Op said RV with 50A power outlet, not Mobile Home. So 550.33(B) does not apply here.
It appears §551.42(D) describes the Op's "50-ampere-rated panelboard." Or 50A outlet §551.72(C)
"50 amperes shall be supplied from a branch circuit of the voltage class and rating of the receptacle."
So a 200A service can feed 50A disconnects with #6cu @ 60ºC, or 75°C rated outlets with #8cu, rather than 3/0 copper.