I want to protect a utility trnasformer with pad from traffic with pipe bollards. Is there any ruling on how far this pipe bollard can be from a transformer?

Thanks for your answer.

[ November 21, 2003, 04:50 PM: Message edited by: jkim780 ]
 

tom baker

First Chief Moderator
Staff member
Re: Utility XFMR protection from traffic

If its the POCO's transformer then they will have standards for you to follow.
If its your transformer then look at section 110.26 in the NEC. The clearance is determined by the voltage.
 

charlie

Senior Member
Location
Indianapolis
Re: Utility XFMR protection from traffic

You need to check on the size also. We require 6" Galvanized pipe or conduit, 7' long set 3' deep in concrete and filled with concrete. These posts are to be set 1' off the corners of the pad in both directions away from the corners of the pad to allow full access to the transformer which will be smaller than the pad. Check out the drawings in our Goldbook. :D
 

jkim780

Senior Member
Re: Utility XFMR protection from traffic

Originally posted by charlie:
You need to check on the size also. We require 6" Galvanized pipe or conduit, 7' long set 3' deep in concrete and filled with concrete. These posts are to be set 1' off the corners of the pad in both directions away from the corners of the pad to allow full access to the transformer which will be smaller than the pad. Check out the drawings in our Goldbook. :D
Thank you, guys.