Utilization equipment

Status
Not open for further replies.
Examples of utilization equipment for the 50 ℅ and 80 percent rules please

IMO:

Window A/C will be 50% utilization equipment.

Portable table saw, chop saw ... would be 80% utilization equipment.
 
You're asking about fastened in place versus not fastened in place?

"15- and 20-Ampere Branch Circuits. A 15- or 20-ampere branch circuit shall be permitted to supply lighting units, other utilization equipment, or a combination of both. The rating of any one cord- and plug-connected utilization equipment shall not exceed 80 percent of the branch-circuit ampere rating. The total rating of utilization equipment fastened in place shall not exceed 50 percent of the branch-circuit ampere rating where lighting units, cord-and plug-connected utilization equipment not fastened"

I'm looking for real world scenario where I would encounter the 50 and 80 percent rule. Thanks for your help
 
(1) Cord-and-Plug-Connected Equipment Not Fastened
in Place. The rating of any one cord-and-plug-connected
utilization equipment not fastened in place shall not exceed
80 percent of the branch-circuit ampere rating.
80% rule would be a table saw, window a/c, microwave, sump pump.


(2) Utilization Equipment Fastened in Place. The total
rating of utilization equipment fastened in place, other than
luminaires, shall not exceed 50 percent of the branch circuit
ampere rating where lighting units, cord-and-plug connected
utilization equipment not fastened in place, or
both, are also supplied.

The 50% rule could be a garage door opener, dishwasher, disposal, etc
 
I'm looking for real world scenario where I would encounter the 50 and 80 percent rule. Thanks for your help

50% rule - bathroom ventilation fan - typically less then 50% of a 15 amp branch circuit - rule doesn't apply here

Now put a vent fan with heater in there - and you usually are more then 50% of a 20 amp branch circuit - can typically only put other non cord and plug connected loads on that circuit.

Another one would be a general purpose multioutlet circuit and you wanted to plug a fixed in place sump pump into that circuit, the pump can't be more then 50% of the circuit rating - so 7.5 amps for a 15 amp circuit or 10 amps for a 20 amp circuit.

80% rule is a little harder to come up with specific application that isn't temporary in nature. If you are going to bring in power tools to remodel a room are you going to run a temporary circuit to avoid violating the 80% rule or do you just learn what can't be run at the same time for this temporary condition?

A shop might be a place to use the 80% rule - but it must be equipment not fastened in place for the 80% to apply. If you have equipment that is rated at 80% of the circuit and it always gets plugged into the same receptacle - chances are you run an individual circuit to a single receptacle for that equipment anyway - in which case 210.22 applies instead of 210.23.
 