Examples of utilization equipment for the 50 ℅ and 80 percent rules please
Examples of utilization equipment for the 50 ℅ and 80 percent rules please
You're asking about fastened in place versus not fastened in place?
80% rule would be a table saw, window a/c, microwave, sump pump.(1) Cord-and-Plug-Connected Equipment Not Fastened
in Place. The rating of any one cord-and-plug-connected
utilization equipment not fastened in place shall not exceed
80 percent of the branch-circuit ampere rating.
(2) Utilization Equipment Fastened in Place. The total
rating of utilization equipment fastened in place, other than
luminaires, shall not exceed 50 percent of the branch circuit
ampere rating where lighting units, cord-and-plug connected
utilization equipment not fastened in place, or
both, are also supplied.
80% rule would be a table saw, window a/c, microwave, sump pump.
The 50% rule could be a garage door opener, dishwasher, disposal, etc
I could argue that either way. I have seen people open a window and stick the unit in then close the window.You would not consider a window A/C a fastened in appliance?
I'm looking for real world scenario where I would encounter the 50 and 80 percent rule. Thanks for your help