stevensmw
New member
- Location
- Portland, Oregon
Recently I replaced added a service disconnect/meter socket to an existing system and added new SE to the utility as it was to short for the new panel. The inspector noticed there was a coupling on the old 50 year old+ service mast and said it needed to be removed. First, if I removed it this would violate the PUD's 18" rule to the roof, but secondly, doesn't the NEC 230.28 Masts as Supports allow for coupling if there is a support to the roof above it such as guy wires? "where the coupling is located above the last point of securement to the building".IE Utilization of couplings for a mast are permitted only below the point the mast is braced, secured, or supported.