Also, looking at the legend, I guess these are supplying 120/208 3-wire "single" phase panels. If all the loads are 120V, this VA method is fine. If there are 208V loads, then dividing those among the two conductors by take 208V * Load Amps to get VA, dividing that by two, and assigning half to each conductor is non-conservative. A conservative method would mulitply the 208V current by 120V and assign that value to each conductor.
Lastly, the breaker size for the 1J power supply is missing.
Cheers, Wayne