hhsting
- Glen bunie, md, us
- Junior plan reviewer
Does any one know if tenant space is vacant then what would be it’s occupancy type building code wise?
Residential was just an example. The point was that, as far as I'm aware, occupancy types don't change whether they are occupied or unoccupied. Yours would be a commercial space, whether occupied or unoccupied.Just wanted to update vacant space is in commercial building with two spaces divided for rent with firewall etc etc as req Not residential building
I would wager it would just move up to a more generalized category such as Business, Mercantile, or generally Commercial. Whatever the building is zoned for.Ok but commercial space has a lot of occupancy types. Do you mean it depends on building occupancy type the building was intended for?
The occupancy type would be business, or group B, assuming the jurisdiction goes by the ICC codes. See 304.1 under definitions.un(occupied)?
The occ type usually starts with the building, whether or not the space is rented, so if it looks like a multi-tenant office building, the occ-type would be office even when vacant/empty. OTOH, if it's part of a strip mall and fitted out as a barber shop, the type type would be barber shop even if not rented.
I suspect this changes state-to-state and maybe even down to the city level. (And I am not a lawyer...)
You originally asked about occupancy as it relates to the building code. This is not very related to occupancy as it relates to the NEC. Somewhere there is a set of architectural plans for this space. On those plans will be a note or some such that clearly identifies the IBC classification of the space. That classification will govern the HVAC, fire protection, fire alarm, egress, fire separation, and a bunch of other requirements for that space. So, which one do you mean, building code or NEC?Please see below link to thread it is not clear if it complies with NEC 2014 section 230.40 exception no. 1 or not and has vacant space
NEC 2014 230.40 exception no. 1 apply here or not
Attached sketch shows building layout bottom left corner, electrical room detail bottom right corner and Riser at top. Building layout shows Vacant space which has not been filled and Tenant A space occupancy type B. In the top middle of layout is electrical room. Electrical room detail shows...forums.mikeholt.com
Ask the local inspection authority...that is the only answer that really matters....
Anyways what is the intent of NEC when it’s saying occupancy IBC or something else
In my opinion most base it on the owners and/or tenants. Each owner and/or tenant gets a meter and their own set of service entrance conductors. With a vacant space, that will typically have its own meter and set of service entrance conductors. The billing would go to the property owner until the space is rented to a tenant.Ok but any opinions on what do most or
Majority of local inspection authority would interpret it as?
However, you really have to ask the inspection authority for the location of the project.