Minuteman
- The Sooner Nation
I posted this thread last year, about a church self contracting a new building.
The "Construction Manager" hired me to install power for his job shack. A few months later he gave me a set of prints for the building. We poured over the prints and sent a (large) bid. Heard nothing.
In July he called me to install temp power. He then gave me a new set of prints and said that they re-sized the job from about 60,000 sq ft. to 40,000 (with contingency for the future). The Mechanical/Electrical prints were done by a different PE than the first prints, and very odd.
The service is still a 208Y, 3000-amp disco with 2000-amp MDP. Why?
A few other issues:
Okay, so we sent a new bid. But I think that the prints could be fixed, and some value engineering could be done. The guy I work for/with knows a ME/EE firm very well and we wired their new office and the EE's new house. Should we put the CM and the ME/EE together before the slab gets poured? The job has not been awarded yet, and I know there are other bids.
- It's about 200' from the disco to the MDP.
- All the A/C equipment is 3 phase.
- The lights are 120v
- There are 5 sub panels located throughout the building.
A few other issues:
- There are identical 4, 3, and 2 lamp fixtures, and several with Emergency ballast. Most rooms are mixed. One office has a 3 lamp and a 2 lamp.
- All the Em-ballast fixtures are located within 6-8' of a regular Em fixture.
- There is 3" PVC under the slab going from the sound booth. Several 3" go up 4" walls, including 2 that are walls with sink plumbing for the main restrooms.
- All restrooms are loaded with 20-amp dedicated GFCI's.
- All the incandescent can fixtures are in high, hard ceilings.