What about the disconnect that is required by 430.102(B)?It is common design practice where I work that if a VFD is provided with a UL Listed approved disconnect then a disconnect is not required between the fan and the VFD.
There are two disconenct rules in 430.102. One for the controller (VFD) and one for the motor. If both the motor and the controller are within sight of the controller line side disconnect, then you only need that disconnect. Any time the motor is not within sight of the controller disconenct, you need a motor disconnect, unless you can comply with one of the exceptions to 430.102(B).430.102 states that you need a means of disconnect ahead of the controller this is provided only if the vfd is not in sight of the disconnect or over 50ft.
rmiller0248@charter.net said:My expirience has always been to have it before feeding the VFD, due to possible damage the other way. Opening / closing between VFD and motor can cause damage??
.
iwire said:Which is a good idea but only possible if the VFD is within sight of the motor.
motorcontrol said:NO. if the vfd is in line of site, disconnect should always be on line side. installing a load side service diconnect on vfd application is not healthy....Only as necessary evil to comply with AHJ......
The controller disconnect must always be within sight of the controller. There are no exceptions to 430.102(A). The motor disconnect must be within sight of the motor unless you meet one of the conditions in the exception to 430.102(B). There was a major change in the wording of the exception a few years back. In the older codes, a remote lockable disconnect was always permitted to be used as the motor disconnect. The current wording has placed major restrictions on the use of a remote lockable disconnect in place of a "within sight" disconnect for the motor.So your saying even if you lock it out it still has to be in sight?
don_resqcapt19 said:Rob,
The controller disconnect must always be within sight of the controller. There are no exceptions to 430.102(A). The motor disconnect must be within sight of the motor unless you meet one of the conditions in the exception to 430.102(B). There was a major change in the wording of the exception a few years back. In the older codes, a remote lockable disconnect was always permitted to be used as the motor disconnect. The current wording has placed major restrictions on the use of a remote lockable disconnect in place of a "within sight" disconnect for the motor.
Don
motorcontrol said:I would say, if the mcc is not in site of the fan, then, install disconnect to comply with nec. if the disconnect on load side of the vfd is opened while the fan is in operation, the vfd will trip anyway. If the fan operation is part of hvac then, you can integrate either the current output or fault output from the vfd to rest of the controls.
petersonra said:Why would the drive care?