JoeStillman
Senior Member
- Location
- West Chester, PA
- Occupation
- Electrical PE
In this scenario, we have three single-phase oil-filled transformers installed in an above-grade vault by the utility company. The primary cables are installed and terminated by the POCO, secondaries by the owner. The transformers have the usual four spades on the secondary, X1, X2, X3, X4. The transformers feed a 4000A switchboard with 9 runs of (4) 750 kCM. Because the transformers are arranged in 208Y/120V secondary, the X1-X3 and X2-X4 lugs are paralleled on each transformer.
On each transformer, how many cables do we have to install between X1-X3? or X2-X4? The outgoing cables can be arranged with 4 on X2 and 5 on X4. Is a single jumper enough to ensure equal current in the coils? I've seen it done with a single jumper and also with 4 jumpers on each phase. Is there some standard I can refer to for advice?
On each transformer, how many cables do we have to install between X1-X3? or X2-X4? The outgoing cables can be arranged with 4 on X2 and 5 on X4. Is a single jumper enough to ensure equal current in the coils? I've seen it done with a single jumper and also with 4 jumpers on each phase. Is there some standard I can refer to for advice?