VAV

"All" is a pretty strong term... I've usually seen the physical VAV boxes drawn on the mechanical pages, but any controls stuff (both the MSTP BACnet link and the 24v/120v or whatever happens to be moving the damper) on an electrical page that's separate from the rest of the "normal" electrical (lighting, 120v cubicle farm, walls and rooms, etc.).
 
The electrical plans need to address the VAVs in some way. The electrical contractor needs to know that the mechanical contractor will be installing them, and the two need to coordinate to get electrical power and controls connected.
 