xptpcrewx
Power System Engineer
- Location
- Las Vegas, Nevada, USA
- Occupation
- Licensed Electrical Engineer, Licensed Electrical Contractor, Certified Master Electrician
I was referring to this table in particular...
Note: The total allowable voltage drop could be considered the difference between minimum service voltage and minimum utilization voltage (as a conservative approach). Whether or not to use Range A or Range B depends on the duration of voltage fluctuation expected. For steady-state applications I would use Range A; for transient motor starting perhaps Range B.
Note: The total allowable voltage drop could be considered the difference between minimum service voltage and minimum utilization voltage (as a conservative approach). Whether or not to use Range A or Range B depends on the duration of voltage fluctuation expected. For steady-state applications I would use Range A; for transient motor starting perhaps Range B.