Question(2) of the week:
Again, I looking for opinions (and the science/industry practices behind them).
The installation
MCC is 480V, 3ph, Z grounded. Motor is 31A, 225LRA, high starting torque load. Feeder is 3 - #6CU, Okonite CLX, MCHL (Al sheath), ~1000ft.
The quandry:
I am looking at the voltage drop under starting current. So I go to Ch 9, Table 9 and use the equation in note 2:
Ze = R cos(θ) + XL sin(θ)
For R, I used the value in the Al conduit column R = .49 ohms. For XL, I used the value in the AL conduit column XL = .051 ohms. For power factor, I considered the load at locked rotor to to be pure inductive, cos(θ) = 0, and sin(θ) = 1.
Which gives Vd@LR = (1.732)(225)(.051) = 20V
For a check, calculating the Vd at FLA. using pf = .85, and the effective Z for CU in Al conduit, Ze = .45 ohms
Vd@FLA = (1.732)(31)(.45) = 24V
The Question: Is this right? It seems strange to me the Vd at LR is less than the Vd at FLA. What am I missing?
Amazingly in the last 35 years this hasn't come up and I really haven't paid much attention to it. Usually I have used I = FLA, pf = .85, Ze from the .85pf column. Probably the first time I have used pf = 0 and Ze = XL. Today it is bugging me. I'm going to dig out my red book and maybe Electric Machinery Fundamentals.
Any thoughts are graciously appreciated.
carl (no code to hide in and not yet understanding the science :-? )
Again, I looking for opinions (and the science/industry practices behind them).
The installation
MCC is 480V, 3ph, Z grounded. Motor is 31A, 225LRA, high starting torque load. Feeder is 3 - #6CU, Okonite CLX, MCHL (Al sheath), ~1000ft.
The quandry:
I am looking at the voltage drop under starting current. So I go to Ch 9, Table 9 and use the equation in note 2:
Ze = R cos(θ) + XL sin(θ)
For R, I used the value in the Al conduit column R = .49 ohms. For XL, I used the value in the AL conduit column XL = .051 ohms. For power factor, I considered the load at locked rotor to to be pure inductive, cos(θ) = 0, and sin(θ) = 1.
Which gives Vd@LR = (1.732)(225)(.051) = 20V
For a check, calculating the Vd at FLA. using pf = .85, and the effective Z for CU in Al conduit, Ze = .45 ohms
Vd@FLA = (1.732)(31)(.45) = 24V
The Question: Is this right? It seems strange to me the Vd at LR is less than the Vd at FLA. What am I missing?
Amazingly in the last 35 years this hasn't come up and I really haven't paid much attention to it. Usually I have used I = FLA, pf = .85, Ze from the .85pf column. Probably the first time I have used pf = 0 and Ze = XL. Today it is bugging me. I'm going to dig out my red book and maybe Electric Machinery Fundamentals.
Any thoughts are graciously appreciated.
carl (no code to hide in and not yet understanding the science :-? )