ptonsparky Tom Location NE (9.06 miles @5.9 Degrees from Winged Horses) Occupation EC - retired Tuesday at 11:32 AM #21 Strathead said: How does the utility? Or any buidling? Click to expand... Stiffer supply.
Knightryder12 Senior Member Location Clearwater, FL - USA Occupation Sr. Electrical Designer/Project Manager Wednesday at 7:49 AM #22 I would just use the FLA of the 45KVa transformer, which is 54.1 amps. Quick VD calc. that I did = #6 cu =3.25%, #4 cu = 2.05%