When you do a vd calc and you have either 120/208 or 277/480 how do you know which voltage to input. e.g. 277/480 which would it be?
The load electrical data tells me that?
Yes. For the case of a 208Y/120 system (the larger number goes first for 3 phase systems), you could have a 2-wire 120V circuit, a 2-wire 208V circuit, a 3-wire 120/208 circuit (this one's a bit tricky, you'd ideally look inside the equipment connected and consider it as a combination of the previous two cases), a 3-wire 208V 3-phase circuit (3 phase voltage drop has a different factor in the formula compared to 2-wire single phase voltage drop), or a 4-wire 208Y/120 circuit (again, you'd ideally look at the loads supplied and consider it as a combination of the other cases).
Cheers, Wayne
Each state has its own energy code and thats where the code requirements for voltage drop are found.
Some jurisdictions still amend the NEC with a voltage drop and minimum wire sizes like NYC and NM.
Id say as of 2025 the majority adopt the ASHRAE Standard 90.1, I believe NJ does;
ASHRAE Standard 90.1 Section 8.4.1 simply states Feeder conductors and branch circuits combined need to be sized for a maximum of 5% voltage drop in total. Service conductors are exempt.
The starting voltage is the 'Nominal System voltage' from NEC 220.5 or ANSI C-84 Table 1
The standard Nominal ones are easy:
120, 208Y/120, 240D/120, 240, 240/480, 277, 480Y/277, 480, 600Y/347, 600, 690Y/400, 690, 2400, 4160Y/2400, 4160.
I used to have a cool chart that had a exhaustive list of standard voltages used in North and South America.
It had the the 'odd' wye 60hz ones 416Y/240, 240Y/139, 220Y/127 and ones various combinations of old 'two phase'.