Chris P
New User
- Location
- Staten Island , New York
- Occupation
- Electrician
Hey guys. I’m been having a problem with two vending machines in a laundromat. Both of the vending machine have no compressor and run about 3 amps. Both machine come on and run for random amounts of time from 30 mins to 3 hours and eventually trip the gfi plug. Both machines have their own dedicated circuit breaker in separate boxes but were feed with a 12/3 cable so they were sharing a neutral. I ran new 2 -12/2 dedicated lines and still the same problem. The customer placed a exstention cord on one machine and plugged it into a different outlet 7 ft away and the machine seems to be running fine. I’m at a loss here and not sure what else I can do. Any help would be greatly appreciated thanks