The line-side of the Main Breaker on a 480v MCC is rated Dangerous (>40 cal/cm2). How would you comply with verify-test-verify to prove the buss deenergized after opening the Breaker? The MCC is also the source to the lighting transformer for the entire building. Thanks
We use a non-contact voltage detector mounted on a hot stick.The line-side of the Main Breaker on a 480v MCC is rated Dangerous (>40 cal/cm2). How would you comply with verify-test-verify to prove the buss deenergized after opening the Breaker? The MCC is also the source to the lighting transformer for the entire building. Thanks
The line-side of the Main Breaker on a 480v MCC is rated Dangerous (>40 cal/cm2). How would you comply with verify-test-verify to prove the buss deenergized after opening the Breaker? The MCC is also the source to the lighting transformer for the entire building. Thanks
As soon as you have done that you will be able to have 'professionals' that can perform work per your Electrical Safe Work Practices.I'm trying to help develop a program to be sure these people are properly trained and have the necessary equipment...
I am a qualified electrical worker in the eyes of my company because they have trained me, not because of my schooling. As soon as I leave this company, I will need to be re-qualified by my new company under their practices.Our guys are very much professionals but not to the level of a EE - although we all are still learning, especially in the light of the requirements of 70E.
I am a qualified electrical worker in the eyes of my company because they have trained me, not because of my schooling. As soon as I leave this company, I will need to be re-qualified by my new company under their practices.
In general, we do not apply safety grounds at 480V.
How do you know if the voltage is off or if the device failed? You still would need to do a L-D-L verification to comply with 70E.