If you check 1910.333(b)(2)(iv) "If the circuit is over 600 volts nominal, the test equipment shall be checked for proper operation immediately before and immediately after this test". Whatever the voltage is, if I have to stick my hands into a piece of equipment that is suppose to be dead, I will do the live-dead-live test.
Some testers for these voltages are capable of performing a self-test. That seems like it would comply with the requirement.