Hello every one I'm watching the videos in EL theory and the panel kept referring to 70B for how the NEC wants us to verify our torch but I cannot find it can any one assist me on understanding this. For reference I am at EL theory unit 6, 10 min and 17 sec into video and page 42 in the work book.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
7.2.1.4.1
When using a calibrated torque wrench to confirm the torque of previously installed threaded hardware, the retightening value shall not exceed 90 percent of the manufacturer’s specified initial torque value.
The use of the term "hardware" makes me think this only applies to bolts that connect busbars or connect a lug to the busbar and not to a set screw that puts direct pressure on a conductor.
 
Location
ca
Occupation
solar
Hey guys I feel really dumb after continuing in the video i realized these are different books that have different rules than the NEC and i thought it was referring to an article in the NEC sorry I'm a new apprentice and just trying to figure it out
 
Location
ca
Occupation
solar
Hello every one I'm watching the videos in EL theory and the panel kept referring to 70B for how the NEC wants us to verify our torch but I cannot find it can any one assist me on understanding this. For reference I am at EL theory unit 6, 10 min and 17 sec into video and page 42 in the work book.
hey guys I saw meant to say torque i apologize man im really making my self look dumb today
 
Location
ca
Occupation
solar
Thank you!!!!! so I'm a lil confused so are the 70b and 70e i kept hearing in the videos apart of the NFPA or something and does the NEC not cover whats in those books?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Thank you!!!!! so I'm a lil confused so are the 70b and 70e i kept hearing in the videos apart of the NFPA or something and does the NEC not cover whats in those books?
The NEC is NFPA 70. 70B and 70E are also published by the NFPA. They are not widely adopted like the NEC is, but 70E is can be cited by OSHA under the general duty clause as it relates to worker safety.
 
Location
ca
Occupation
solar
Wow I went back to felling extremally dumb I'm so used to the trade term NEC and never paid attention to what the book is actually titled. wow hopefully my lead Doest happen to see this ill never hear the end of it lol what article can i look up how to properly test for torque
 
There have been quite a few threads here about torque, but the main and often missed point is that you can't "verify" torque on a bolt after it's been set! Sure, you can put the torque wrench/screwdriver to it and see if it clicks, but all that will tell you is that it's loose enough to move, not that was correct; the only way to see that it's right is to loosen and tighten to torque again. (Look up "sticktion" for this.)

Snap-on has some words about the subject-
 

Joethemechanic

Senior Member
Location
Hazleton Pa
Occupation
Electro-Mechanical Technician. Industrial machinery
Yeah tourque should be measured while in motion. Some other factors that throw touque values out the window are any damage to the threads, and anything applied to the threads (like oil) but it could be anything. Usually manufacturers will either say to torque clean and dry, or they will specify what the threads should be coated with. This is important because although your torque may be correct, what is on the threads alters the clamping force of the fastener
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
There have been quite a few threads here about torque, but the main and often missed point is that you can't "verify" torque on a bolt after it's been set! Sure, you can put the torque wrench/screwdriver to it and see if it clicks, but all that will tell you is that it's loose enough to move, not that was correct; the only way to see that it's right is to loosen and tighten to torque again. (Look up "sticktion" for this.)

So, really there is no way to verify to an inspector that the fastener or lug has been torqued to specification.

-Hal
 