If separate neutrals are required and not breaker ties how would YOU run the MC cable(not pipe) in the field to these 1P-20A receptacles?
1.Wall with 3 separate circuits you would not andcould not run the cable horizontal through studs you would run vertical fromeach receptacle to ceiling, correct? Even if it were 2 circuits you couldn’t.If you have 12/3 your hots are good but you only have 1 neutral. Guess if you used FMC then you could pull another neutral.
2.Wall with 3 receptacles on same circuit youcould run horizontally to each receptacle.
1.Wall with 3 separate circuits you would not andcould not run the cable horizontal through studs you would run vertical fromeach receptacle to ceiling, correct? Even if it were 2 circuits you couldn’t.If you have 12/3 your hots are good but you only have 1 neutral. Guess if you used FMC then you could pull another neutral.
2.Wall with 3 receptacles on same circuit youcould run horizontally to each receptacle.