ramsy
NoFixNoPay Electric
- Location
- LA basin, CA
- Occupation
- Service Electrician 2020 NEC
Doesn't NEC 215.2(A)(1) require 750 MCM (377 x 1.25) if motor is a continuous load?Won't fit in my conduits anyways, so looks like I'm going to go with 500 MCM..... And I need to review this stuff a little more