We are installing automation in a C1D1 area, and the integrator calls (from Italy) calls for Shielded Cable. Of course the cabinet is in the unclassified area 70+ feet away. Flexible Cord is permitted because the application is a mixer (501.140(A)(1)), but we intend to run cables for two motors together in IMT except where flexibility is needed.
Since 400.8(6) prohibit using flexible cord in raceways. How can I maintain the shield, and provide seals at the firewall.
VFD Cable in Class 1
We are installing automation in a C1D1 area, and the integrator calls (from Italy) calls for Shielded Cable. Of course the cabinet is in the unclassified area 70+ feet away. Flexible Cord is permitted because the application is a mixer (501.140(A)(1)), but we intend to run cables for two motors together in IMT except where flexibility is needed.
Since 400.8(6) prohibit using flexible cord in raceways. How can I maintain the shield, and provide seals at the firewall.
iwire said:Yes VFD cable, I have only used it once.
But in the little I have read they do want shielding, a metal raceway usually takes care of this.
The one time I used VFD cable was in a very large control cabinet, it was my understanding at the time the engineer was concerned with the VFDs un shielded output would create problems with the other electronic devices in the same cabinet.
Soon I will actually be shielding some VFD conductors for testing purposes.