kwired
Electron manager
- NE Nebraska
- EC
There are VFD's out there with 120 V single phase input and 240 three phase output. About 1 Hp max is all you will find, but the application typically only uses 1/3 -1/2 hp motors so not a problem.If I'm understanding this correctly, they want to use a VFD to act as a transformer, and then a second VFD to do phase conversion and drive the pump? I'm fresh out of school so there's a vast collection of things I have yet to see, but this seems overly complicated...and expensive. Just to pick some brains:
-Wouldn't it be much more cost effective to use a transformer for 120-230V?(Assuming there's a rated enclosure involved)
-If there's already 480V available, couldn't a single 480V drive set to output only 230V accomplish the same task?
It would be less complicated and less expensive to just use a 480 volt drive to begin with, 480 volts is normally the supply voltage to this application.