VFD and motor - Low RPM
W@ttson
NJ-USA
PE
Hello,
I have a general question regarding VFD operation with a motor.
Suppose a motor has an FLA of 100A. It is rated at 460V 60Hz.
Now suppose you want to run the motor at 6hz. To maintain you V/Hz ratio, since you load is the same, your voltage would decrease to 46V. Now if the same power is being delivered to the motor, I would assume that the current to the motor would need to increase.
P = I*V*sqrt(3)*PF
For same P, with decreased V, the I would be inversely proportional.
What if this increased current is greater than the FLA of the motor? Say the current measured to the motor is 130A. Is there risk to the motor? I assume not since the duration of operating the motor would only be 30 min or 60 min or if it were continuous it would have a blower on it.
Any insight on this where I might be missing something would be appreciated.
Thank you
The power delivered to the motor depends on the shaft load. What kind of load do you have that is constant HP as you slow it down?
You can (roughly speaking) get constant torque at lower than nameplate speeds. So available HP will drop proportional to the speed.
its a hoisting application. its a constant torque load. I guess I shouldn't be seeing constant KW going to the motor with difference in speed then.
This is true, but you normally don't deliver constant power at variable speed. Mechanically, the power delivered is the product of angular velocity (which you are turning down) and torque. To require constant power mechanically, that means the torque required would have to go UP. That normally doesn't happen.
Yeah, now I am confused.
My data shows the following:
full speed = 900rpm
Voltage = 460V
Current = 75A
KW = 22KW
10% Speed = 90RPM
Voltage = 52V
Current = 142A
KW = 11KW
if the power reduced (not sure why by 2), why is the current so high?
full speed = 900rpm
Voltage = 460V
Current = 75A
KW = 22KW
10% Speed = 90RPM
Voltage = 52V
Current = 142A
KW = 11KW
Are the hoist/motor/drive all part of a factory assembly?
Also, how are you measuring these data points?
full speed = 900rpm
Voltage = 460V
Current = 75A
KW = 22KW
10% Speed = 90RPM
Voltage = 52V
Current = 142A
KW = 11KW
In condition 1, assuming the motor is idealized as 100% efficient, I calculate an output torque of 233 Newton-meters.
In condition 2, with the same assumption, I calculate an output torque of 1167 Newton-meters. About 5 times the torque load.
This is what I've inferred, using P = omega*tau for mechanical power, where omega is the RPM translated to radians/second, and tau is the torque.
Condition 2's current/voltage/power figures are consistent with what I'd expect, which indicates a power factor of 86%. I'm skeptical of the 75A current figure in condition 1. Using 460V and 22 kW electrical, and the same power factor as condition 2, I calculate 25.6A as the current I'd expect for condition 1. Perhaps 75A is the sum of the currents on all 3 phases, rather than the current per phase. Standard arithmetic sum of RMS values, rather than vector sum.
This is about 1/5th of the current of condition 2. Current directly determines the output torque, so I'd expect 5 times the torque to imply 5 times the current.
This is the problem with too high of a Volts-to-Hertz ratio. The Hertz and motor geometry, directly determine the maximum possible RPM of an AC motor. The only other place for the power to go, is the motor torque, which draws more current as a direct consequence.
I think there is a bust in the values that I was given. Something is not adding up as you show.
I referenced some data from a motor test shop and that showed exactly what I expected to see as seen in the discussions here and on similar posts like this.
For the same torque, you should see the same current at different speeds for a constant torque application. If you reduce the speed, you reduce the power on the output of the drive.
On the input of the drive for the same reduced output power the current will be less because you maintain the same voltage on the input of the drive, in this case 460V.
Before I retired I PM'ed , troubleshoot, and replaced & installed VFD'S in a large hospital/research centers. I only worried about the current at the 480 volt supply. I cross checked the line ampere on Danfoss LCD ( local control display ) & ABB VFD'S with my Fluke VOM. Voltages & ampere were always within 1% of the display verses hand held meters. with modern drives having a switching speed up to 5,000 Hertz and output not a perfect wine wave never found an analog ( old amprobes ) or digital clamp on amp meter that could read drive out put current. What are you using to read such a sky high output current? I called amprobe up back in the 1980's why our digital 300 amp clamp on meter was unable to display accurate readings on various VFD'S. Told me they were only good for 60 Hertz. Several drive techs recommended as a general rule not to run pumps below 20% of motor RPM.
I assumed he was reading the output values from the VFD, but that was just an assumption. You know what they say about assumptions. LOL
The hoist needs torque, not kW. Torque will remain relatively constant with current (other than a little more losses at slower speeds).
The mistake in your calculated values is that you are thinking of kW as an electrical value. Motor kW is a mechanical value of torque at a given speed. kW = tq (N-m) x RPM / 9550. Forget the voltage, it’s irrelevant here. So if you maintain a constant torque (and thereby somewhat constant current), then reduce the speed, the kW goes down.
full speed = 900rpm
Voltage = 460V
Current = 75A
KW = 22KW
10% Speed = 90RPM
Voltage = 52V
Current = 142A
KW = 11KW
different power factor I would assume?
When the motor is operating this slowly, you bump into non-linearities that you typically get to ignore.
1) Slip. Remember that for the motor to operate at 900 RPM, the synchronous speed is probably higher than 900 RPM. (Approximately) to get the same torque at a different speed you need the same slip (not % slip, but absolute slip in RPM). So to operate at 10% speed the motor is being driven at > 10% frequency.
2) Resistance. The idea of 'constant V/Hz' assumes that the inductance of the motor limits current flow. But at low frequency you can't ignore resistance. When you operate at 10% frequency you need >10% of base voltage to compensate for resistance.
3) Motor torque and heat production. Roughly, if the motor is operated at the correct voltage for the frequency, torque is proportional to drive current. Doesn't matter if you are operating at full speed or using the motor to hold position at zero speed; torque is proportional to current. And heating is proportional to the square of the current. So when you operate at reduced speed and increased torque you expect increased heating.
4) Short term overload. On instrumented motors in a lab in the 10-20hp range, I've operated them at 100% overload (2x rated torque) for 15-30 minutes before excessive temperature rise. This meant that the motor was on the path to overheating and failure, but we stopped the operation before the insulation was too hot. If the motor starts cold, then I'd expect motor in the 20-50hp range to tolerate 30% overload current for quite a while before the winding temperature becomes excessive.
In your reported data, the VA in 'low speed' is 21% of the VA in 'high speed', but the power in KW is 50%. That number seems suspicious to me. If you are talking about electrical power input, that implies a huge change in power factor that I don't expect, and if you are talking about mechanical power that implies a huge change in torque. So I'd dig further before trusting the numbers.