I need to go back to the building to check the fault code, but I am just thinking about all the possibilities for now. Also, the FLA of the motor is 22.9A but the maximum spike was 140A. Could this maybe have caused it?I would be surprised if you didn't have distortion on the load side.
What is the fault code telling you?
You need to know what the parameters are for the VFD.I need to go back to the building to check the fault code, but I am just thinking about all the possibilities for now. Also, the FLA of the motor is 22.9A but the maximum spike was 140A. Could this maybe have caused it?
How was the 140A maximum spike measured?I need to go back to the building to check the fault code, but I am just thinking about all the possibilities for now. Also, the FLA of the motor is 22.9A but the maximum spike was 140A. Could this maybe have caused it?
fluke meterHow was the 140A maximum spike measured?
How was the 140A maximum spike measured?
Check to see if the meter reads true RMS Amps. If not, the meter won't be accurate. Wish I knew which way it will be off... Anyhoo, the amps reading from the VFD is probably the most accurate.fluke meter
My rule of thumb in measuring the output of a VFD with a meter is that if the meter cost you less than 4 figures to the left of the decimal point, it’s going to give you relatively meaningless data.Check to see if the meter reads true RMS Amps. If not, the meter won't be accurate. Wish I knew which way it will be off... Anyhoo, the amps reading from the VFD is probably the most accurate.
The meter I have cost about $5000 each, I monitored the load and line side of the VFD lolMy rule of thumb in measuring the output of a VFD with a meter is that if the meter cost you less than 4 figures to the left of the decimal point, it’s going to give you relatively meaningless data.
I wonder if one of the 1960s era HP VTVMs would give at least a semi-accurate reading, I think I saw some of them at Urban Ore (Berkeley, CA) recently.My rule of thumb in measuring the output of a VFD with a meter is that if the meter cost you less than 4 figures to the left of the decimal point, it’s going to give you relatively meaningless data.
How well did it compare with the VFD?The meter I have cost about $5000 each, I monitored the load and line side of the VFD lol