timm333
- Minneapolis, MN
- Electrical Design Engineer
NEC 430.122(A) says minimum size of breaker for VFD is 125% of the rating of VFD. What is the maximum size of breaker that can be used for VFD?
Actually, you will find that unless you are using VFDs sold by companies that also make MCCBs, the VFDs might not be UL listed for use behind circuit breakers at all, you might need to use fuses. So the only valid answer is to RTFM and see what the VFD manufacturer tells you is the correct size of breaker; if it is listed to be used with a breaker, it typically will only be listed with one. If they don't say anything, it's a safe bet that it's because they can't and you have to use fuses.