Pump installer called me about a VFD and a different installer. 3rd hand service call? Question is about VFD cable being used with a submersible. The installer did not use on load side as instructions suggested/required and the VFD has failed. Is that a typical fail or is it more inclined to the motor or cable?
I suggested the installer was SOL for failing to install per instructions, regardless.
NO drive requires VFD cable. None of that cable is rated for submersible use. That’s a complete load of crap.
I’ve seen others used but the most common submersible cable is type THW. Some people, mostly mining, use type W. It is surge tested to 2.2 kV by spec. We’ve used it for years, VFD or not. There are major reasons NOT to use a VFD with a submersible having to do with bearings and cooling design issues.
Hands down if a VFD failed due to non-use of a VFD cable, it’s time to rotate manufacturers. It really is quite that simple. First thing to check is your available short circuit current and the VFD rating. Also realize that VFDs are not that hardy, don’t like dirt/dust/humidity/heat/frost, and are very intolerant of crappy power.
But given that THHN which is thinner tests to 2850 V as per NEMA testing, I suspect this is very low. Given that the motor will be rated 1000-1400 V and surge test below the cable surge test, it seems like the VFD cable spec is a load of crap. The other argument is that somehow a rounded cable in a jacket will develop less asymmetrical shunt capacitance, enough to make a difference. I routinely measure motor performance, dozens of motors per month. I look for current imbalances like that as well as common mode currents. Guess why I often see common mode currents? Maybe because a VFD by nature outputs common mode currents!! Far more than you will get from even some pretty bad wiring jobs.
Those are the major claims. The rest are such a joke it doesn’t bear repeating. And yes the purveyors of this load of crap are companies like Allen Bradley, Belden, Alpha, and more. This is one of those things where if someone brings it up, escort them off the plant site with security and contact legal and purchasing.
At around 100+ feet there is a problem with VFDs called reflected waves. The distance is slightly affected by shielded wiring. When I say shielded wiring I mean surrounded by a metal covering such as a conduit. It does not require VFD cableThis is a real issue. The solution is to use a dv/dt filter which is fairly small and cheap. This increases the limit to over 1000 feet. But if you ignore this issue it destroys motors, not VFDs.