VFD conductor sizing

Status
Not open for further replies.

Ingenieur

Senior Member
Location
Earth
Can we stick to the topic please?

Now that is the kettle calling the pot black

the topic has 2 paths
1 op is correct andvinput is 112 and that is resolved: conductor is 1.25 x 112 , cb = 125 A
2 op is incorrect so we can't proceed until he clarifies
 

Davebones

Senior Member
The drive is a Invertek Drive ( Optidrive CP2 Model : ODP-2-64075-3HF4NTN ) I physically haven't seen this drive . This is the information one of our departments sent me . It shows input ratings ( supply current continuous 112.5 amps ) . Output ratings ( output current 110 amps ) .
 

Besoeker

Senior Member
Location
UK
The drive is a Invertek Drive ( Optidrive CP2 Model : ODP-2-64075-3HF4NTN ) I physically haven't seen this drive . This is the information one of our departments sent me . It shows input ratings ( supply current continuous 112.5 amps ) . Output ratings ( output current 110 amps ) .
Seems like the wrong way round but what do I know......
 

Ingenieur

Senior Member
Location
Earth
The drive is a Invertek Drive ( Optidrive CP2 Model : ODP-2-64075-3HF4NTN ) I physically haven't seen this drive . This is the information one of our departments sent me . It shows input ratings ( supply current continuous 112.5 amps ) . Output ratings ( output current 110 amps ) .

manual: http://www.invertekdrives.com/clien...82-P2MAN-IN Optidrive P2 User Guide V1.20.pdf
output 110 pg 9
input 116.9 pg 151
CB 160 A pg 151

many drives I looked at had the input I slightly higher than the output
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
The drive is a Invertek Drive ( Optidrive CP2 Model : ODP-2-64075-3HF4NTN ) I physically haven't seen this drive . This is the information one of our departments sent me . It shows input ratings ( supply current continuous 112.5 amps ) . Output ratings ( output current 110 amps ) .
Then yes, you must size the conductors for 125% of 112.5. The breaker size is whatever they say it must be per their UL file. Mfrs based here will typically give you a min-max range or at least a maximum, but it all depends on how they submitted it to UL and foreign companies often don't fully understand. Looking at an Invertek manual, that appears to be the case here; only one breaker size listed (125A) and it specifically says that for UL installations, you must use that breaker.
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
Looking at an Invertek manual, that appears to be the case here; only one breaker size listed (125A) and it specifically says that for UL installations, you must use that breaker.

The manual I looked at says for a 75HP drive, 125A c/b for NON-UL applications and 150A c/b for UL applications.
 