That you disagree with me is fine, fun, and expected.
Not you personally
your baseless assumptions
:thumbsup:
Engineers typically do not operate like that
Can we stick to the topic please?Not you personally
:thumbsup:
Agreed.Now that is the kettle calling the pot black
the topic has 2 paths
1 op is correct andvinput is 112 and that is resolved: conductor is 1.25 x 112 , cb = 125 A
2 op is incorrect so we can't proceed until he clarifies
Seems like the wrong way round but what do I know......The drive is a Invertek Drive ( Optidrive CP2 Model : ODP-2-64075-3HF4NTN ) I physically haven't seen this drive . This is the information one of our departments sent me . It shows input ratings ( supply current continuous 112.5 amps ) . Output ratings ( output current 110 amps ) .
Then yes, you must size the conductors for 125% of 112.5. The breaker size is whatever they say it must be per their UL file. Mfrs based here will typically give you a min-max range or at least a maximum, but it all depends on how they submitted it to UL and foreign companies often don't fully understand. Looking at an Invertek manual, that appears to be the case here; only one breaker size listed (125A) and it specifically says that for UL installations, you must use that breaker.The drive is a Invertek Drive ( Optidrive CP2 Model : ODP-2-64075-3HF4NTN ) I physically haven't seen this drive . This is the information one of our departments sent me . It shows input ratings ( supply current continuous 112.5 amps ) . Output ratings ( output current 110 amps ) .
The manual I looked at says for a 75HP drive, 125A c/b for NON-UL applications and 150A c/b for UL applications.
| ODP-2-64075-3HF4N |
his exact PN is in this manual http://forums.mikeholt.com/showthread.php?t=186926&page=4&p=1861741#post1861741
pg 9
ODP-2-64075-3HF4N
non UL 160 A CB (or fuse)
UL 150 CB (or fuse
pg 51
The more up-to-date manual...(Revision 2.10 instead of Revision 1.20)
says 125A Non-UL and 150A UL.