Hey everybody,
I've got a 10HP motor (fed from 3 phase 208V Y panel) for a bag filter/dust collector that I'm hooking up (Nederman S1000). After reading through all the installation manuals I am now confused.
The Nederman S1000 (dust collector) comes with a VFD (with a start/stop button and programming screen).
According to the dust collector manual I would need an 80A inverse time breaker or a 60A dual element time delay fuse (fused disconnect).
FLA- 26.3A
x 250%= 65.75 (80A breaker inverse time breaker)
x 175%= 46.025 (60A time delay fuse)
*if this was just a basic contactor setup with start/stop there'd be no questions, it's the addition of the VFD that is putting me into analysis paralysis
Now according to the VFD manual for a 10HP motor I need to setup a fused disconnect for the VFD with 40A high speed class J fuses.
The question,
If I provide a fused disconnect with 40A J Class fuses for the VFD, am I still sizing the breaker at 80A? Does the breaker need to be an inverse time breaker? (If I were to guess, the answer would be yes for both)
Between the VFD and the motor do I still need to put in another fused disconnect for the motor with 60A time delay fuses? (Motor, vfd and all disconnects would be within close sight of one another) Or will the single fused disconnect for the VFD (40A class J fuses) suffice?
I've got a 10HP motor (fed from 3 phase 208V Y panel) for a bag filter/dust collector that I'm hooking up (Nederman S1000). After reading through all the installation manuals I am now confused.
The Nederman S1000 (dust collector) comes with a VFD (with a start/stop button and programming screen).
According to the dust collector manual I would need an 80A inverse time breaker or a 60A dual element time delay fuse (fused disconnect).
FLA- 26.3A
x 250%= 65.75 (80A breaker inverse time breaker)
x 175%= 46.025 (60A time delay fuse)
*if this was just a basic contactor setup with start/stop there'd be no questions, it's the addition of the VFD that is putting me into analysis paralysis
Now according to the VFD manual for a 10HP motor I need to setup a fused disconnect for the VFD with 40A high speed class J fuses.
The question,
If I provide a fused disconnect with 40A J Class fuses for the VFD, am I still sizing the breaker at 80A? Does the breaker need to be an inverse time breaker? (If I were to guess, the answer would be yes for both)
Between the VFD and the motor do I still need to put in another fused disconnect for the motor with 60A time delay fuses? (Motor, vfd and all disconnects would be within close sight of one another) Or will the single fused disconnect for the VFD (40A class J fuses) suffice?