drktmplr12
Senior Member
- Location
- South Florida
- Occupation
- Electrical Engineer
This is a shot in the dark, but quick enough to ask.
I know this is a loaded topic!
I am tasked with preparing a technical document explaining why water production wells were failing and restarting while running on generator power during and after Irma. This occurred in Southeast Florida.
I am not asking the forum to provide me a dissertation, that is my job. I am more looking for simple (and probable) theories to consider from the informed opinions on the forum. I will provide any additional information that is requested, granted I can easily get my hands on it.
Thanks in advance for anyone who takes the plunge here.
My current theories:
FPL AB 486V, AC 486, BC 486
Gen. AB 514, AC 514, BC 514
Wacker G125 Prime Rated, 98/122kVA @ 0.8 pf
Well 29, 175 HP
FPL AB 483V, AC 483, BC 483
Gen. AB 480, AC 480, BC 480
CAT 350/437kVA @ 0.8 pf
I know this is a loaded topic!
I am tasked with preparing a technical document explaining why water production wells were failing and restarting while running on generator power during and after Irma. This occurred in Southeast Florida.
I am not asking the forum to provide me a dissertation, that is my job. I am more looking for simple (and probable) theories to consider from the informed opinions on the forum. I will provide any additional information that is requested, granted I can easily get my hands on it.
Thanks in advance for anyone who takes the plunge here.
My current theories:
- Process conditions caused wells to experience overload conditions, causing VFD protections to trigger. The motor cooled down and automatic restart triggered. The cycle repeated until operations intervened.
- Generator became unstable due to harmonics resulting in overvoltage conditions. The VFD would fault, generator would stabilize and automatic restart triggered. The cycle repeated until operations intervened.
- Failures were observed while wells were operated with portable generator power.
- Wells may or may not be on same utility feed.
- Same behavior at all wells with VFD (Altivar 61)
- Well controls have been equipped with VFD’s for approximately 5 years.
- Wells controlled by VFD have been operated on generator power previously and without incident.
- It has proven difficult to repeat the behavior with the same generators.
- Data gathered includes generator nameplate data, electrical data (voltage, power, harmonics), VFD configuration parameters and flow measurements.
- The configuration parameters one VFD was downloaded to be inspected for possible causes for VFD failures.
- A fault log for one drive was obtained, which revealed a series of overvoltage faults without time stamp. These could have happened before, during or after the storm.
- Automatic restart is enabled.
- A Dranetz Power Platform 4300 Spectrum Analyzer was used to measure voltage and harmonics present at each site.
FPL AB 486V, AC 486, BC 486
Gen. AB 514, AC 514, BC 514
Wacker G125 Prime Rated, 98/122kVA @ 0.8 pf
Well 29, 175 HP
FPL AB 483V, AC 483, BC 483
Gen. AB 480, AC 480, BC 480
CAT 350/437kVA @ 0.8 pf