drktmplr12
Senior Member
- Location
- South Florida
- Occupation
- Electrical Engineer
I would be looking for two additional information factors, the drive manufacturer's consultation or instructions about running on generator power. It's possible the drive's trip settings can be relaxed for generator power. And the generator manufacturer's consultation or instructions about running straight into a 100% front end rectifier load. What problem that may cause that the manufacturer may know about (voltage regulation, distortion).
For example, if half of the load was straight running line connected three phase motors, they would provide some buffering or rotating line conditioning to mitigate the line effects of the big non linear rectifier load. Without that there was no buffering or line conditioning.
Are you assured the generator was always on and connected and it was the drive that tripped. Is it the sense that the drive tripped from detecting a distorted supply that itself caused.
I have consulting with SQD and generator manufacturer's to discuss the interactions from both sides. That is good advice.
I am under the impression the generators were always on the the drive tripped to protect itself from distortion that it caused or some process related condition that overloaded the motor.