When considering VFD's for contribution to a fault in a short circuit analysis what magnitude of fault current is usually considered. For example lets say I have an MCC which feeds a 200HP VFD which in turn feeds a disconnect and 200HP motor.
I know if the VFD has a bypass switch then the fault current contributions from the line and load side (motor contribution) is considered to simply bypass the VFD and is unaffected and usually represents the worst case for fault analysis.
What about when a VFD bypass does not exist? Will the VFD pass all or a portion of the line side contribution through the VFD? Is there only a certain percentage of the fault current that is let through from the line side since the line side voltage is converted to a DC voltage first before is it converted back to an AC voltage?
Typically I have heard that most VFD's will not pass fault contribution from the load side (motor contribution) unless the VFD is a regenerative type VFD. Does this mean that if a VFD is not of the re-generative type that it will not pass any current from the load side to line side? Is this due to the DC conversion in the VFD?
I know if the VFD has a bypass switch then the fault current contributions from the line and load side (motor contribution) is considered to simply bypass the VFD and is unaffected and usually represents the worst case for fault analysis.
What about when a VFD bypass does not exist? Will the VFD pass all or a portion of the line side contribution through the VFD? Is there only a certain percentage of the fault current that is let through from the line side since the line side voltage is converted to a DC voltage first before is it converted back to an AC voltage?
Typically I have heard that most VFD's will not pass fault contribution from the load side (motor contribution) unless the VFD is a regenerative type VFD. Does this mean that if a VFD is not of the re-generative type that it will not pass any current from the load side to line side? Is this due to the DC conversion in the VFD?