You can't miss something that wasn't there in the first place.
There is no guaranteed answer.
In most cases the power electronics will sense the output fault and shut down the inverter.
In some cases the drive will act as a 'fuse' when the current flow through it causes drive components to fail in an 'open' mode.
Then there where be the rare occasions when the drive components fail in a shorted mode and the fault contribution can be substantial.
He does. I just need teach him to aim better.:thumbsup:
.................
But when you are away, does he miss you?
So I guess for fault analysis purposes if there is no bypass switch you just assume that there is 100% let-through on load side of drive? I cant really think of a reason why you would only want to use a smaller % of the let-through expect perhaps if you were evaluating Arc Flash at a downstream disconnect and wanted to look at a minimum case? Like you mentioned though the drive will likely shut itself down on a fault before an external protective device so I don't know what you would use for clearing time to calculate Incident Energy on the load side of VFD.
It sounds like for analysis purposes if there is not a bypass you don't consider regenerative contribution on the line side from the motors unless you know specifically that the drive is a regenerative drive.
I'm with you on this, but just want to add that most drives will allow at least 200% current for about 3 seconds, long enough to be noticeable in an incident energy situation. The 150% rating is for 1 minute (on constant torque rated drives).Wasn't the OP question about fault current from the motor?
... Therefore the incident energy would usually be based on 1.1 times the drive rating (maybe as high as 1.5x). ...
Wasn't the OP question about fault current from the motor?
As far as let through to a fault, I would treat it as if nothing flows through the VFD, unless there is a bypass contactor.
If the VFD components are functional then its electronics will prevent fault current from flowing towards the motor, in a manner similar to how they prevent startup current from flowing. There fore the incident energy would usually be based on 1.1 times the drive rating (maybe as high as 1.5x). BTW, I use the same philosophy with a UPS, although bypass is pretty common on medium and large units..
You are correct I don't normally worry about the motor contribution. Even if the drive is a regenerative type, is would have to be in a decelerating mode and the current would pretty much be limited to 1.5x.
I'm with you on this, but just want to add that most drives will allow at least 200% current for about 3 seconds, long enough to be noticeable in an incident energy situation. The 150% rating is for 1 minute (on constant torque rated drives).
Were does the 1.1 or 1.5 times the drive rating come from? Is this the typical maximum current that a drive will output even during a fault?
With a regenerative drive, during a fault on the line side of the drive the motor would pass fault contribution through the drive regardless if it was decelerating or not?
The 1.1 or 1.5, or the 2X (from jraef) are based on the amount of current the electronics can supply to the load. Check with the manufacturer, but the value is small.
If the fault is on the line side of, or internal to, the VFD then no current will flow towards the motor.
If the fault is on the load side of the VFD, its electronics will usually shut down the drive resulting in no current flow. If the drive does not shut down, its electronics will limit the current to its design parameters, in a manner similar to how it limits motor starting current.
A regenerative drive primarily only feeds back into the grid when the DC bus voltage is too high, which typically only occurs during deceleration (although an overhauling load could also be a factor).
A line side fault would be seen as a loss of incoming power so most drives will turn off and 'coast to a stop'.