Are you using those Lenze 4X drives with an integral rotary disconnect and ethernet/wifi capabilities?
In the last 2 years we've installed almost 140 of those Lenze 4X VFD's in two different dairies.
The electrical engineer for the project had us put these VFD's/fans on 30 amp circuits with a handful of VFD's on each circuit. No supplemental protection installed, even though I HIGHLY recommended individual OCPD so one bad drive will not take down the whole string.
To date, they've had no less than 8 VFD's fail in less than two years, tripping the breaker and of course, killing power to the rest on the circuit.:happyno:
I have not personally replaced any myself, I've had the guys do it, but I'm told the failures they're seeing are burns/scorch marks right at the 480v terminals with the internal drive wiring.
The really silly part is, shutting the integral disconnect off does not take the damaged drive out of the system allowing the others to run, as the problem is the internal factory wiring on the line side of the disconnect.
Fortunately, we did not supply the drives so the repair costs are on someone else.
They did not like my price for supplemental protection with manual motor protectors, I'm hoping you have better luck than I did with your customer.