Hey forum, had an interesting incident at work that I had never seen before. We had a motor on a VFD (around 200hp-300hp) go to ground. As a result, ALL of the closed WL breakers in the upstream 3000A Siemens switchgear showed high amps (around 1500-2000 amps), including the main. The feeder breakers eventually tripped out on LT. We put a power meter on the load side of the main, and saw this amperage didn't exist. This is on a delta, ungrounded 480V system. Once we narrowed down which VFD caused this, we megged the wires going to the motor/motor itself and found the ground.
We know that the VFD should have detected the ground and tripped, but what I find interesting is all of the breakers in the Siemens gear showing this "ghost" amperage. We had all the breakers primary injection tested and they passed. Has anyone seen/heard of anything like this happening before?