ptonsparky
Tom
- Occupation
- EC - retired
In a way I was hoping to find all sorts of dust to clean up. If there was, it’s deeper than I wanted to go.
I don't know if it's the same product that we have here called Air Duster. If so, a word of caution. It is flammable. My daughter got a bit of a fright when she got flames coming out of her laptop. The lesson is don't use it on live equipment. I just thought ptonsparky ought to made aware of that.
Wouldn't the GF detection actually require a fault to ground? is it measuring a change of current in an amount of time that would ignore the basic smell test?
Yeah, this was true on that size of drive; it was a batch of CTs on the output that were made by Honeywell and they are bad in that they fail prematurely. If it does fall into that date code, A-B will rebuild the drive for free, but if it outlasted the warranty (which it would have by now because this was 2-3 years ago), they will have to pay the freight costs. Running without a load on it by the way is not a valid test, but they could put ANY load on it, i.e. a small little motor.Owner made some phone calls & he got a quicker response then I did. I wasn't forcing the issue yet until after we replace the conductors from vfd to motor. (You guys don't know how lucky you are sometimes to live in more populated areas. Finding parts in stock is a nightmare. I had more than 5 of my suppliers. I had 3 2/0 crimp lugs, they had 0.)
Depending on mfg date there is an issue with the frame size we have. The drive ran for about a day and half again before it faulted this morning. Owner was going to disconnect the load side conductors and turn the drive back On. If it faults, new drive. At the moment it's running with no load.
Yeah, this was true on that size of drive; it was a batch of CTs on the output that were made by Honeywell and they are bad in that they fail prematurely. If it does fall into that date code, A-B will rebuild the drive for free, but if it outlasted the warranty (which it would have by now because this was 2-3 years ago), they will have to pay the freight costs. Running without a load on it by the way is not a valid test, but they could put ANY load on it, i.e. a small little motor.