I have a client who wants a VFD put into an existing MCC. It's an R1 frame (7.5HP) VFD. Is it possible to do this? I typically would not put a VFD in an MCC, rather have a fusible disconnect in the MCC feed the VFD mounted near the motor, but the client is insistent on having it in the MCC.
Assuming I have the bucket space in the MCC, how would this work?
How important is it to adhere to the rules?
If it is important, you CANNOT put a VFD in an MCC, unless it is a VFD that was designed, tested and listed
BY THE MCC MFR to retrofit into their MCC. Given that you mention an "R1 Frame" I will assume it is an ABB ACS550 drive. ABB only released their line MCCs this year, so I would hazard a guess that you do not have an ABB MCC. So if it is any other brand, there is no
legal way for you to mount a VFD in it and maintain the UL listing and Short Circuit rating of the MCC. And with an MCC, the SC rating for the entire MCC cannot be greater than the lowest rating of any unit in it. So even if you accept the concept of the "courtesy" 5-10kA rating you can have for something untested, that low rating will extend to all other parts of that lineup.
That's not to say it is not done all the time, because it is. If the job is not going to be inspected, and the company's insurance policy has no requirements for using only UL listed equipment, you can do what you want.
Without testing though, you are kind of on your own for what it is going to take to do it, especially with regards to heat rise testing. One trick you could do though is to get a quote from ABB for a single section of THEIR new MCC with that specific drive in it and see what size cubicle
they would use. It's not perfect because you don't know if your MCC will have the same air flow, but it's a good place to start.
Or if the existing MCC is not too old, you could just forgo the ABB drive and get a legal add-on bucket from the original mfr. If by chance it is a Rockwell (Allen Bradley) MCC, the age would not matter.