A reactor is the first line of defense. A passive harmonic filter is a reactor plus capacitors, tuned to absorb a specific harmonic, followed by another reactor (L-C-L filter). The goal in reducing harmonics, although full of variables, can be thought of as trying to control the Voltage total harmonic distortion (V-THD) by limiting the Current total harmonic distortion (I-THD) which is what non-linear loads like VFDs create. So if you can keep your I-THD from the VFD to 5% or less, you are all but guaranteed to meet IEEE-519 voltage distortion limits at the PCC (Point of Common Coupling).
Quick list of options in order of effectiveness (also generally cost as well):
For reference, a VFD with
no reactor, no DC bus choke (DC bus choke is like a reactor but inside of the VFD on the DC bus):
80-120% I-THD, meaning the current flowing in the circuit at harmonic frequencies can actually EXCEED the normal working current of the motor.
Remember,
the GOAL is 5% I-THD or less;
- VFD with line reactor, OR a DC bus choke: 30-35% I-THD
- VFD that has a DC bus choke AND a line reactor ahead of it: 20-25% I-THD
- VFD + Passive Harmonic Filter, tuned to the 5th harmonic only: 7-10% I-THD, tuned to the 5th and 7th: 6-8% I=THD
- VFD with 12 pulse front end: 7-10% I-THD*
- VFD with 18 pulse front end: 5-6% I-THD*
- VFD with Active Front End (AFE): <5% I-THD
- Active Harmonic Filter (AHF) connected to the same AC input circuit as the VFD (at PCC): <5% I-THD
*
Multi-pulse front-end drives require voltage balance between phases to be <1% to meet these values. At >1%, harmonic mitigation diminishes.
Either way. VFD mfrs (or panel builders) can package the reactor or filter for you, or you can get them stand-alone in their own enclosure and wire it yourself. Multi-pulse and AFE drives come built that way, AHFs are always a separate unit that connects at the PCC.