430.122A requires conductors supplying power conversion equipment be sized at 125% of the rated input to the equipment.
For a VFD with separate line reactor - is the line reactor included as part of the 'power conversion equipment'? And therefore the conductors are 125% of line reactor rating as well? I assume yes, and actually this isn't a big deal.
430.130 (A) says that Branch-circuit short circuit device can be sized per 430.52(C)(1). I interpret this to mean that the OCPD setting can be higher than the ampacity of the conductors between OCPD and drive. Although there are some historical posts i have seen which suggest conductors between OCPD and drive need to be protected at their ampacity.
What if the line reactor is installed - is this considered part of the 'power conversion equipment'?
Example - 100 HP motor, 100 HP drive rated 117A input, vendor specifies max inverse time CB of 375A.
Conductors require ampacity 117 x 1.25 = 146.25A or 1/0. I believe 430.130 says the 1/0 can be protected by the 375A breaker.
If we add a line side reactor - does this change the OCPD requirements for the circuit?