I reviewed a set of vendor control panel drawings - panel has single power feed, tapped from the input distribution block to four individual VFDs within a Hoffman enclosure.
The design included line reactors installed on the line side of each VFD's overcurrent protective device - so there was no isolation or OCPD between the input distribution block (protected at 400A) and the individual reactors.
Is this a normal configuration? I'd assume the line reactor would typically be between the OCPD and drive. But I don't see many multi-VFD drive cabinets, maybe there is a reason they laid it out this way.
The design included line reactors installed on the line side of each VFD's overcurrent protective device - so there was no isolation or OCPD between the input distribution block (protected at 400A) and the individual reactors.
Is this a normal configuration? I'd assume the line reactor would typically be between the OCPD and drive. But I don't see many multi-VFD drive cabinets, maybe there is a reason they laid it out this way.