VFD mitigate harmonics?

Same term used for two totally different things. When talking about fall of potential testing on a breaker you are measuring the voltage drop under load from the line side to the load side of the breaker. The result is typically millivolts. The biggest indicator of a problem is where the readings of voltage drop are substantially different between phases of the same device.
Usually there is a simple fix. Just cycle the breaker on and off a few times. The wiping of the contacts is usually all it takes.
 