tony_psuee
- PA/MD
There are several things that differentiate a motor to be inverter duty;
1. increased insulation value, typically 1600V versus 1000V
2. additional phase paper between the windings
3. larger rotors, accounting for the larger size of an inverter versus non-inverter duty
The issue with the reflective wave causing a motor failure is more common with motors running at 460V. On a 460V VFD, the VFD DC bus is around 660-680V. I have measured line to line almost 1200Vp-p at the motor on 225ft +/- lead length. I have seen consultants specify 230V on applications were the lead lengths will be long with non-inverter duty motors. Even with reflective wave the motor usually never sees a spike that exceeds the 1000V insulation rating. Fractional motors are more at risk because a NEMA standard does not exist for them. IMO you get what you pay for, use a cheap VFD with a cheap motor and you get an expensive installation to maintain. In my experience, the most important recommendation to follow on a VFD installation is the grounding requirements.
Tony
Tony