We're having some trouble with VFD powered temporary equipment running through a 300kVA step-up transformer, from 208 to 480V. Machine specs shows 354A peak, 257A rated. Constant motor start/stop, with limited run time in between (hoist). Control system faults out when starting the hoist. We changed the transformer out for a 400kVA unit, and no more problems.
What I can't get straight is if the transformer size is actually causing undue voltage drop, triggering the fault. I wouldn't think there should be a problem at 282kVA (at 354A), and the transformer should be able to absorb an overload anyway. What I don't yet have is historical data on actual current and voltage at the drive, but I'm working on that.
Can the non-linear effects cause this? We have to use a grossly oversized generator when running this equipment, but that's for other reasons. This application is on utility power.
I don't want to use a blanket recommendation for an 'oversized' transformer without some justification, other than one bit of success, as the customer has to supply and connect the mains and transformer. And I can't be sure the transformer was the actual cure.
I've searched the web and this site, and found nothing to suggest that VFD's, as a general rule, require special treatment in transformers. Can anyone shed any light on this?
What I can't get straight is if the transformer size is actually causing undue voltage drop, triggering the fault. I wouldn't think there should be a problem at 282kVA (at 354A), and the transformer should be able to absorb an overload anyway. What I don't yet have is historical data on actual current and voltage at the drive, but I'm working on that.
Can the non-linear effects cause this? We have to use a grossly oversized generator when running this equipment, but that's for other reasons. This application is on utility power.
I don't want to use a blanket recommendation for an 'oversized' transformer without some justification, other than one bit of success, as the customer has to supply and connect the mains and transformer. And I can't be sure the transformer was the actual cure.
I've searched the web and this site, and found nothing to suggest that VFD's, as a general rule, require special treatment in transformers. Can anyone shed any light on this?