TwoBlocked
Senior Member
- Location
- Bradford County, PA
- Occupation
- Industrial Electrician
I am pretty sure of my diagnosis and remedy, but want to check with you fine folks in case I am missing something. A 25HP 3-ph 480VAC VFD driven motor driving an axial fan was tripping out the VFD on overcurrent. Meggerd fine, but had uneven resistance phase to phase. disconnected all the leads. Each lead read fine by itself, but some were shorted to others. Obviously an internal short, but why, and what to do about it.
The length of the motor leads are over 100ft and the rule of thumb I am used to is to anything over 100ft needs an output filter on the VFD to avoid voltage spikes shorting out the motor windings. There are four of these unit at the facility and because of the configuration of the equipment, It is necessary to bring in a large crane to replace one of these motors. The one that went bad has the longest motor leads.
So do you fine folks think it is likely that an VFD output filter would have prevented this fault. Do you think all the VFDs feeding these motors should get VFD output filters?
The length of the motor leads are over 100ft and the rule of thumb I am used to is to anything over 100ft needs an output filter on the VFD to avoid voltage spikes shorting out the motor windings. There are four of these unit at the facility and because of the configuration of the equipment, It is necessary to bring in a large crane to replace one of these motors. The one that went bad has the longest motor leads.
So do you fine folks think it is likely that an VFD output filter would have prevented this fault. Do you think all the VFDs feeding these motors should get VFD output filters?