Depends on a LOT of factors., it's all over the map. Some manufacturers publish that data, others ignore it and leave it to the end user to find out on their own.
Here is a document from Rockwell that shows THEIR tested distances from Drive to Motor for each different VFD line they sell (or sold). If you pick out a single size, let's say 10HP 480V with
1200V winding insulation (non-inverter duty), you get the following from their tables:
PowerFlex 523... with nothing between the drive and motor, 40ft; add just a load reactor, 300ft; with a DV/DT filter, 1000ft.
PowerFlex 753... with nothing between the drive and motor, 40ft; add just a load reactor, 300ft; with a DV/DT filter, 1200ft.
But if you use minimum "
NEMA MG-1 part 31 inverter rated" insulation of 1488V:
PF523... 300ft, 1000ft, 1000ft
PF753... 350ft, 1200ft and 1200ft
So note that the thing that makes the MOST difference is the motor insulation value. Once you step up to the 1488V insulation, the DV/DT filter makes no difference.